You have three UPS systems connected in parallel. The UPS systems have an imbalance in the load sharing of approximately 20%.

What should you recommend?

Show Suggested Answer Hide Answer
Suggested Answer: A

An imbalance in load sharing between UPS systems connected in parallel can often result from unequal cable lengths to the common busbar. If the cabling from each UPS to the busbar varies significantly in length, it can lead to differences in impedance, resulting in uneven load distribution. Ensuring that cable lengths are consistent helps to balance the load sharing across the UPS systems.

Detailed Explanation:

Parallel UPS systems rely on uniform impedance to share loads evenly. Differences in cable lengths cause variations in resistance, leading to one or more UPS units carrying a disproportionate share of the load. Standardizing cable lengths ensures equal impedance, which promotes balanced load sharing and prevents one UPS from being overburdened, thus maintaining overall system reliability.

EPI Data Center Specialist References:

EPI guidelines recommend checking cable lengths when load imbalances occur in parallel UPS configurations. Ensuring equal lengths is a common method to resolve impedance issues that affect load distribution, which is critical for the stable operation of redundant power systems.


Contribute your Thoughts:

Chara
23 days ago
Harmonics and common mode noise? Nah, man, that's like trying to fix a flat tire by changing the radio station. Cable lengths all the way!
upvoted 0 times
...
Donte
24 days ago
Option B? Really? That's like saying a 20% imbalance in your bank account is 'no reason for concern'. Definitely go with A.
upvoted 0 times
Denny
3 days ago
User 1: Option B? Really? That's like saying a 20% imbalance in your bank account is 'no reason for concern'.
upvoted 0 times
...
...
Martina
1 months ago
Hmm, 20% imbalance? That's like trying to balance a see-saw with an elephant and a chihuahua. Better check those cable lengths!
upvoted 0 times
Deangelo
8 days ago
D) Review the harmonics levels within the computer room
upvoted 0 times
...
Christiane
11 days ago
C) Review the common mode noise levels within the computer room
upvoted 0 times
...
Kaycee
24 days ago
A) Review the cable lengths of each UPS to the common busbar
upvoted 0 times
...
...
Lynette
1 months ago
A 20% imbalance in load sharing is definitely a concern. I would recommend reviewing the cable lengths to the common busbar as per option A.
upvoted 0 times
Marva
12 days ago
User 4: Let's make sure to check that out as soon as possible.
upvoted 0 times
...
Twana
18 days ago
User 3: Yeah, that imbalance in load sharing could cause issues if not addressed.
upvoted 0 times
...
Tiffiny
22 days ago
User 2: Agreed, that sounds like the best recommendation.
upvoted 0 times
...
Bette
1 months ago
User 1: I think we should review the cable lengths of each UPS to the common busbar.
upvoted 0 times
...
...
Alida
1 months ago
I agree with Micaela, it's important to ensure proper load sharing for efficiency.
upvoted 0 times
...
Micaela
1 months ago
I think we should review the cable lengths of each UPS to the common busbar.
upvoted 0 times
...

Save Cancel